Rating:
Display Modes |
#121 | |
If you set up an equation for both states, you get the following: P1V1 = nRT1 P2V2 = nRT2 P1V1/T1 = nR P2V2/T2 = nR P1V1/T1 = P2V2/T2 Now you need to make some assumptions. For our purposes, it's reasonable to assume that starting temperature and pressure will be 20C and 1atm respectively. We know the final temperature gets to about 95C. Now if we assume that the system does indeed reach 3 bar, we can calculate how much the volume changes on relative terms. V1/V2 = P2T1/P1T2 V1/V2 = 3 * 293 / 368 V1/V2 = 2.38 and V2/V1 = ~0.42 That means for the pressure to reach 3 bar, the volume of air must decrease to 42% of its starting value. If we know the volume of air in the ET when cold, we can verify whether or not this actually happens by calculating how much coolant expands during operation. If it's enough to create 3 (or more) bar, then we know the cap does something. Last edited by TerraPhantm; 10-07-2012 at 04:23 PM. |
#122 |
Off topic: Is the exp. Tank cap known to fail? I have overhauled my cooling sys. but the cap is still original. Do I need to worry?
#123 |
Weagle Weagle
#124 | |
Apparently my posts are not long enough for some people to understand. lol. Let me put this into context for those who are still using 2 sets of P and T or having difficulty understanding what the law says. No need to start making assumptions once you have the temperature reading. For example, no need to assume 1 atm at 20 degrees, as the atmospheric pressure depends mostly on the altitude, not temperature. You may have a situation where you fill up the system at -40 degrees near the sea level, in which case, atmospheric pressure will still be 1 atm. P is unknown. V is arbitrary, assume a realistic starting volume, let's say 0.5 L. It will cancel out regardless. n is the amount of substance in moles. R is the gas constant = 8.314 J/(K*mol), meaning it takes 8.314 Joules of energy to raise 1 mole of gas's temperature by 1 degrees Kelvin. T is the temperature reading from the coolant temperature sensor (thanks for the correction on the location). Assume 96 degrees Celcius = 369.15 Kelvin (the latter is the unit used in the equation). We also know that 1 mole of air occupies 22.4 L of air. 0.5 L air will have 0.02223 moles of air in it (n=0.5/22.4). P = (0.5/22.4) * 8.314 * 369.15 / 0.5 = 137.014 Joules/L Using 1 L = 1 dm^3 = 0.001 m^3, we have: P = 137.014 J / 0.001 m^3 = 137,014 Pa = 137.014 kPa = 1.37014 bar... This is the pressure of the air in the expansion tank without taking into account the expansion of the coolant. Assuming the coolant will expand so as to fill half of the empty space in the ET, it follows, from P1/V1 = P2/V2 (special form of the ideal gas law that is valid after the maximum operating temperature is reached, after this point on, I assume T will be constant at 96 degrees Celcius), that this pressure will double to 2.74 bars... If one does not allow the necessary space for the coolant to expand, it again follows, from P1/V1 = P2/V2 that arbitrarily large pressure can be reached. Of course, the pressure will be relieved whenever it reaches 3 bars as long as there is air left in the system, but if there is not air left, the the cap or ET will give up at some point due to high pressures of the liquid pushing against the cap. I hope the math, and my conclusions, are clear now.
![]() Sapphire Black MetallicNatural BrownSilver Cube e46 330i ZHP/ZCW/6MT - Sold HellrotDove Grey e36 ///M3 - RIP Alpine WhiteTanSand High Gloss e46 330i SunRoofLess/5MT For Sale: $300 winter wheel/tire set (sport edition F7s and Dunlop graspics) For Rent: RTAB Removal/Installation and Preload Tools Last edited by SeanC; 10-07-2012 at 04:42 PM. |
#125 |
My Ride: '06 330CiC, '03 M5
Jesus, just get a pressure gauge and connect it to the bleeder port or modify an expansion tank cap. Then measure the max pressure.
All the math in the world will not answer the problem as there are a number of assumptions being made and many times either the assumptions are incorrect, inaccurate or you just fail to take something else into consideration. This also assumes you do not make any basic mathematical errors.
Fuel pump failures - http://forum.e46fanatics.com/showthread.php?t=929501 Temp Info - http://forum.e46fanatics.com/showthread.php?t=964491 Hidden OBC Menu - Check Voltage, Temps, Fuel Level - http://forum.e46fanatics.com/showthread.php?t=239619 E46/E39 GM5 Door Lock Info - www.bmwgm5.com Lower hose fan switch O-ring - BMW #13621743299 |
#126 | |
Weagle Weagle
#127 | |
#128 | |
Sent from my SGH-I997 using Bimmer App
![]() Sapphire Black MetallicNatural BrownSilver Cube e46 330i ZHP/ZCW/6MT - Sold HellrotDove Grey e36 ///M3 - RIP Alpine WhiteTanSand High Gloss e46 330i SunRoofLess/5MT For Sale: $300 winter wheel/tire set (sport edition F7s and Dunlop graspics) For Rent: RTAB Removal/Installation and Preload Tools |
#129 | |
#130 | |
Without going out and buying a pressure gauge and without sacrificing any parts, we have verified that the system can get pressurized to 3 bar with reasonable parameters. So that answered the question as to whether or not the cap makes a difference. If the math is so offensive to you, then leave the thread. Don't take out whatever issues you may have against us. |
#131 |
Thanks Terra, I am familiar with the ideal gas law, I was just trying to figure out what SeanC was values he was using to get his answers. Here's what I get for being mr. streetsmart without calculations.
![]() Volumetric expansions of coolant: dV = V0 B (t1 - t0) B Water = 0.000214 1/°C B Ethylene Glycol = 0.00057 1/°C V0 of E46 Cooling System = ~8.4L t1 = 100°C t0 = 0°C Solving for 50/50 coolant mix dV = 8.4*.5*(0.000214+0.00057)*(100-0) dV = .329 Liters Required Change In Volume to get a 2 bar increase in pressure: Using a modified ideal gas law on the remaining air in the expansion tank(as so clearly explained by TerraPhantm) to find the ratio reduction in expansion tank volume: V2/V1 = P1T2/P2T1 P1 = 1.013 Bar P2 = 3.013 Bar T1 = 273.15 K T2 = 373.15 K V1 = Volume of coolant at 0°C and atmospheric pressure V2 = Volume of coolant at 100°C and atmospheric + 2 bar for expansion tank cap V2/V1 = (1.013*373.15)/(3.013*273.15) V2/V1 = 0.459 or 45.9% So, only factoring the volumetric expansion of coolant with temperature, and the ratio of air before and after coolant expansion to reach the expansion tank venting pressure, the minimum volume of air required to prevent venting through the cap is: V2 = V1 - dV = V1-.329 V2/V1 = .459 Solve for V1 V1 = .608 Liters minimum of air in expansion tank to prevent reaching vent pressure. V2 = .279 checking work, .279+.329=.608, .279/.608=.459; good There will be some expansion of the block and hoses which will decrease the volumed required a small amount, my guess would be something in the range of .1L or less. Interpretation of results: Thinking about this value and looking at the expansion tank, I'd guess the minimum volume is very close to to amount of air that is in the expansion tank when it's properly filled. If you go to a lower pressure radiator cap, you are going to be venting pressure every time the car heats up, and then pulling a little bit of air back in every time the car cools down, and you will lose a small amount of coolant every time through evaporation. With BMW's setup, it seems like the pressure gets very close to the the limit of the expansion tank but doesn't surpass it to prevent very slow coolant losses over time. Also, with keeping the pressure higher, and having the minimum amount of air volume required, when your engine starts to overheat, the system pressure will increase faster to reduce boiling, and the higher pressure gives a greater safety margin before there is some serious boiling and localized heating, which creates warping. Everything could be modified for a lower pressure, but you just decrease your engine's temperature safety margins, and you will need to increase the expansion tank volume prevent losing however small amount of coolant every warmup and cooldown cycle. Damn these BMW engineers, I think they are actually pretty darn crafty, even when it comes to something as small as an expansion tank! It's a shame they didn't make the expansion tank just a little bit stronger. |
#132 |
Where is E46 Mango?? I'm sure he knows the answer if the new cap is a good or bad idea. After all he is The Cooling Officer!!
#133 |
Weagle Weagle
#134 |
WD, I got that! I'm talking about 2 bar versus 1 bar debate and all the math formulas you guys are throwing around :-)
#135 |
Hey guys im doing an experiment on my car where i drive around with no expansion cap on, no oil cap on, a cheeseburger in the passenger seat and the fuel filler cap not screwed in as well. I will be driving under hard and soft circumstances. I will let you guys know how it turns out.
#136 |
wtf, is nobody going to try and prove me wrong, and did I really not make any mathematical mistakes?
...or did everyone just really not care that much about this thread and was really bored and had time to write long posts? |
#137 | |
Not sure I agree with your conclusion though. Higher overall temperatures will only increase the risk of warping. If the boiling point was lower, the overall temperature will not exceed the boiling point until the coolant is converted to a gas. |
#138 | |
I only wish you did it before so we didn't have to do it.
#139 |
Weagle Weagle
I looked at it and your numbers were reasonable to me.
#140 | ||
Though the temperature of the coolant may not go passed the boiling point, the formation of vapor drastically reduces heat transfer from the metal of the engine to the coolant, so the engine will get much hotter than the coolant. Once a vapor bubble or pocket forms, the heat transfer rate goes from 0.58 watts per meter-kelvin to 0.016 , 97% slower. So pretty huge difference in cooling if there is a vapor pocket somewhere. Quote:
![]() Ok, if people aren't going to argue with me, I'm just going to leave. Last edited by mkodama; 10-11-2012 at 12:52 AM. |